Pre wire
#1
Pre wire
I have an opportunity to run wire in my basement (we are presently finisihing the basement) to the outside for a hot tub. Not sure what size a tub we will be getting at this time. What is the best thing to do so that we are ready with the electrical when we decide to go with the tub?
#2
Run 1" PVC conduit with a pull rope in it. You can put the wire in later when you buy the hot tub and know its exact requirements. It will probably end up being three copper #6 plus insulated ground.
#4
Any kind of rope will do. Something you can pull pretty hard on without breaking it. But if the rope you install today is too light for the job later, you can always use the rope you put in today to pull a heavier rope through later, and then use that rope to pull the wire through. Even if the rope breaks, it's not fatal, since it's not that bad to put in a new rope by sucking through some new fishing line later.
Three 90s isn't bad. Four is the most allowed. Gentle sweep 90s will help. The more bends, the larger conduit you might want to use to ease future pulls.
Three 90s isn't bad. Four is the most allowed. Gentle sweep 90s will help. The more bends, the larger conduit you might want to use to ease future pulls.
#6
As long as you limit yourself to no more than 9 current carrying conductors in one conduit, and as long as the conduit is plenty big enough (using no more than about half the capacity), you can put more wires in.
#8
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes
on
0 Posts
N ote that you are not allowed to run low voltage cables in the same conduit (such as TV/Cable, telephone, intercom, computer, etc). Nor should you, even if it were allowed.