Hi,
I am roughing in for a central vac system and want to make sure that the wire size is sufficient. The unit will be 240 on the voltage and 10.7 max amps. . It will be sitting in the basement and the run will be about 40 feet away from the main panel. I was going to run 12 gauge and wanted to double check this will be sufficient. Thank you
 
Sponsored Links
  #2  
Old 05-05-05, 04:19 AM
ElectricalMan's Avatar
Member
Join Date: Feb 2005
Location: Harrisonburg
Posts: 744
One,

That should be fine......I am hoping you are talking about the electrical plug and not the wire run to each recep. port that you plug the hose into as that does not need to be 12 AWG.....that usualy is between 14 and 18 stranded...and usually comes in a 2 wire roll......kinda like extention cord wire.

However, if you are talking about the electrical plug supply to the equipment then a 20A circuit is all you should need so 12 AWG is fine.
 
  #3  
Old 05-05-05, 04:30 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
12 gage wire should be fine. However, what you really need to do is to examine the central vacuum system. It will tell you the proper circuit size, which is probably 20 amp in this case. You then base your wire size on the circuit size and the length of the run.
 
  #4  
Old 05-05-05, 05:05 PM
Member
Thread Starter
Join Date: May 2005
Location: CT
Posts: 36
Thanks for the input, I ran the 12 gauge from the panel to where the unit is going to be hung in the basement.
 