old work ceiling box question

I recently learned that a Carlon old work ceiling box is not intended to support a celing light fixture. Go figure? Anyway, I would like to know your practical experience with this. I installed one in my bathroom ceiling while trying to clean up other wiring problems. I hope to gut the bathroom in the next year and will have it replaced at that time. Any horror stories about old work ceiling boxes? It is only supporting a couple pounds.

Here is what I thought was the fixtures box from the attic: http://i6.photobucket.com/albums/y22...p/04d5716d.jpg

Here is what I found when I removed the light fixture (Oh My!): http://i6.photobucket.com/albums/y22...p/6574527d.jpg
Someone moved the light fixture after the ceiling was dropped down a little bit. The light fixtures mounting strap was screwed to a scrap of casing set on top of the drywall.

There was no access to the wiring in the box. It had a few too many wires in it (12 conductors): http://i6.photobucket.com/albums/y22...p/867abb17.jpg
 
Sponsored Links
  #2  
Old 05-22-05, 07:56 AM
Mr Fixit eh's Avatar
Member
Join Date: Dec 2004
Location: Ontario, Canada
Posts: 94
Received 0 Votes on 0 Posts
If you are keeping the present wiring configuration, you can replace the old electrical box in the attic with an extra-deep box and make up your splices, running a short length of cable to the new, old-work box.

The Carlon box will not support a ceiling fan or heavy light fixture, but it should support a lightweight light.
 
  #3  
Old 05-22-05, 10:27 PM
Member
Thread Starter
Join Date: Sep 2000
Location: Tujunga, CA, USA
Posts: 209
Received 0 Votes on 0 Posts
Thanks Mr. FixIt,
I will leave oldwork box be for the time being and it will be on my to do list to address latter. I found this problem when I went to disconnect some cables that are no longer used. In the approximate location of the original box, I now have a 4" square box that has the cable fished down to the old work box for the light. The box has 4 cables (8 conductors) that only serve the bathroom so I don't need and deep box or extender.

Funny thing about mentioning ceiling fans, I was debating how to support an existing ceiling fan. Then, I became curious as to how much weight these light duty old work boxes can support. I did not think much since it relies on the drywall for support. But I was suprised when Carlon's website said it couldn't support any fixture in a ceiling and 6 pound fixture in a wall.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: