240v GFCI?

I am installing a 240 dedicated circuit with one receptacle in my garage for a table saw. I have a few questions regarding GFCI protection:

1. Does this circuit require GFCI protection?
2. This circuit does not have a neutral. Yet the GFCI breakers that I have found all have taps for the neutral. I am assuming that in my case, I leave those taps emply and only wire in the two hot leads. Is this right?

Thanks!
 
Sponsored Links
  #2  
Old 05-31-05, 09:16 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,332
A dedicated 240V receptacle in the garage does not require GFCI protection at all. Save a large amount of cash and get a standard double pole breaker.
 
  #3  
Old 05-31-05, 09:52 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
As was stated, no GFCI is required.

For a 240 volt GFCI, if the circuit has no neutral then you attach nothing to the neutral terminal.
 
  #4  
Old 05-31-05, 12:30 PM
Skapare's Avatar
Member
Join Date: Jun 2004
Location: USA
Posts: 198
Originally Posted by racraft
For a 240 volt GFCI, if the circuit has no neutral then you attach nothing to the neutral terminal.
Do be sure to connect the white pigtail lead to the neutral bus in all cases. This also supplies 120 volt power for the electronic circuitry inside the GFCI breaker.
 