Shared Neutral Kitchen Circuits

Good Morning!

I have a situation in a kitchen remodel in which I'm planning on meeting the requirements for my two 120V - 20A small appliance countertop circuits by utilizing one 12/3 wiring run. My initial understanding of this was that I should utilize two 20A single pole breakers on separate bus bars, then alternate the use of my red and black "hots" at every other receptacle. Is this correct? Should I be using a 20A double pole breaker instead? Will I be able to get GFCI monitoring ability from my receptacles with the shared nuetral? If so, are the connections any different than a 12/2 circuit? Any thoughts on this is greatly appreciated.
 
Sponsored Links
  #2  
Old 06-03-05, 06:48 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
To do what you propose, you would need to make each and every receptacle a GFCI receptacle, and make all connections on the line side of the GFCI.

Your other alternative is to use a 240 volt GFCI circuit breaker. These are a bit pricey, but might be cheaper than the number of GFCI receptacles you need.
 
  #3  
Old 06-03-05, 06:48 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Using 12/3 and a multiwire circuit would indeed fulfill the U.S. requirements for two small appliance circuits. However, multiwire circuits and GFCI make uneasy bedfellows. Doing it this way would require you to either: (1) Use a GFCI receptacle in every outlet (i.e., no downstream protection available), or (2) use an expensive double-pole GFCI breaker.

So it's up to you. Two runs of 12/2 would be easier and cheaper, but you can use the 12/3 and one of the two options above if you want.
 
  #4  
Old 06-03-05, 11:27 AM
C
ceflyer
Visiting Guest
Posts: n/a
Thank you both, for the speedy and informative replies. I was planning on installing all GFCI receptacles individually protected anyway, so this should work out fine. The two single pole breakers should go on separate legs, right?
 
  #5  
Old 06-03-05, 11:33 AM
M
Member
Join Date: Dec 2000
Posts: 510
Received 0 Votes on 0 Posts
I would recommend using a double pole breaker. This will guarantee that each side of the shared neutral circuit is on opposite phases (absolutely required) and that both sides are de-energized when the breaker is shut off or trips (highly recommended).
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: