GFCI voltage problem
Old 06-13-05, 12:54 PM
kjudson
I have two outdoor GFCI cuircuits, one on either side of my entry staircase. I recently installed low-voltage lighting and used a seperate xfmr for each side of the staircase. The lights work on one side & not the other and after troubleshooting, the non working side worked when I used an extension cord from the "good" side & plugged the xfmr from the "bad" side into it.
I next used a digital dvm to check voltage from both GFCI circuits and found that the "good" side read 123VAC, the "bad" side read 109VAC - 110VAC. I was unable to get ANY AC device (radio, light, etc) to work on the "bad" side but they all worked on the "good" side.
Do I have a neutral that's worked it's way loose/ broken? If not, any idea what the problem could be?
Thanks,
kjudson
Old 06-13-05, 01:01 PM
Certainly sounds like a loose wire of some sort. Did you measure voltage between the hot and the ground also, or just between the hot and the neutral?
Old 06-13-05, 01:36 PM
kjudson
racraft
Thanks for your reply. Between hot & neutral: ~123VAC, hot & ground: ~120.7VAC, neutral & ground: ~10VAC. I'm not all that familiar w/house wiring so I'm not sure what these numbers indicate. Please let me know if you have any suggestions.
Thx,
kjudson
Old 06-13-05, 01:38 PM
kjudson
racraft
Correction: between hot & neutral: ~109VAC - 110VAC
kjudson
Old 06-13-05, 01:48 PM
If you have only 109 volts between hot and neutral, but a full 120 between hot and ground, then you have an open neutral and you are reading phantom voltage.
Put away your DVM and either buy an analog multimeter or use a simple tester or a regular receptacle tester.
Now go find and fix your open neutral.
Old 06-13-05, 01:55 PM
kjudson
racraft
Thx for the advice. I appreciate your quick response. Tough part now willbe to figure out where the neutral break is.
Thx again,
kjudson