so, last night, the power in my room went out. it happened right after i try to turn on one of the floor light which is plugged to a wall unit. the room flickered, then blacked out. checked the circuit breaker, but it is still in good working order (i even swapped with a new one). so today, i took the wall unit apart and trying to check for current. i used the volt meter to check the black and white wire... nothing, then when i connect the volt meter between the ground wire and the black, it'll light up, and same thing when i connect the ground wire with the white wire... i know this is not normal... anybody have any idea what's wrong with my circuit?
Old 06-15-05, 04:54 AM
You have an open neutral.
Old 06-15-05, 05:44 AM
Agree. You have an open neutral(white).
It could be in any device on the circuit even one that is still working. If your receptacles use the backstab connections that is a good place to start your search. Move all the wires to the screw terminals.
Old 06-15-05, 10:15 AM
taz105
thanks guys,
well, how will moving the wires to the screw terminals help? if i see a burnt receptacles, should i just replace it with a new one instead?
Old 06-15-05, 10:33 AM
Backstab connections are notorious for failing. The cause of your open neutral id probably a failed backstab connection. When you pull the receptacles to check them, it will only take you a few minutes to move any backstabbed connection to the screw terminals.
Yes, if you find a burned receptacle (or any other damage for that matter), you should replace the receptacle.