For a small house, I'm calculating the Electrical loads as follows:

1300 sq.ft. x 3 watts = 3900 watts
Dishwasher @ 1200 = 1200 watts
Disposal @ 800 = 800 watts
3 outdoor outlets @180 = 540 watts
---------------------------------------
6440 watts total

6440/230 = 28 amps

Does this mean that a 40 amp service would be sufficient?
Is there a minimum service size regardless of the calculation?

Note that this house has a Gas Range, Gas wall heater and a Gas Dryer. There is a Refrigerator/Freezer and a Microwave but no major fixed electrical appliances other than listed above.
 
Sponsored Links
  #2  
Old 06-15-05, 11:56 AM
Member
Join Date: Oct 2004
Location: USA
Posts: 719
" Is there a minimum service size regardless of the calculation? "

That's a question you need to ask your city.
My city, it was 100 amp I think it went up to 125 amp.
 
  #3  
Old 06-15-05, 02:52 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 5,599
You will not get insurance if the house has less than 100 amp service.
 
  #4  
Old 06-15-05, 05:32 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,441
The National Electrical Code calls for a 100 amp minimum.

In your calculation you left out the 2 small appliance kitchen circuits and the laundry circuit.
 
  #5  
Old 06-15-05, 09:12 PM
Member
Thread Starter
Join Date: Jan 2005
Location: United States
Posts: 455
Originally Posted by pcboss
The National Electrical Code calls for a 100 amp minimum.

In your calculation you left out the 2 small appliance kitchen circuits and the laundry circuit.
You're right so I add another 4500 watts. The calculation then results in a total of 10940 watts.

10940/230 = 48 amps

NEC minimum of 100 amp service or whatever the city requires will govern.
 
  #6  
Old 06-16-05, 01:30 PM
ElectricalMan's Avatar
Member
Join Date: Feb 2005
Location: Harrisonburg
Posts: 744
I have to tell you.....Regardless of the SQ Ft...in todays home we do not put in anything less than 200A service. Cost wise not that much of a difference between a 100A and a 200A service these days.....

With new homes their is always the possible need for expansion and so on and when it comes to figuring a smaller home...or firm simply always goes 200A or more if needed depending on the size of house we are doing.

Yes, the NEC says the service has to be 100A minimum so regardless of your calculations you need a 100A service minimum....but do the math and look at the 200A service panels......Home line or GE ( we use Square D QO ) but the homeline and GE brands are fine.

Now some will argue..I am sure but let me tell you.......we charge very close to the same for a 200A as we do a 100A.....of course we buy the 200A units larger amounts since we split them between my brother any myself...but still it has more options.

Just a thought......
 
  #7  
Old 06-16-05, 01:53 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
I will absolutely concur about a 200 amp service. I can't remember the last time I did a 100 amp service.
We have many modest homes in the area that are all gas and can "get away" with 100 amps. With service replacements some do go this way, but not very many.

I always knew there was a 100 amp minimum service as per the NEC. I completely forget where it is in the book though. Who has the Art.# ?
 
  #8  
Old 06-16-05, 02:08 PM
ElectricalMan's Avatar
Member
Join Date: Feb 2005
Location: Harrisonburg
Posts: 744
Speedy.

We are still in the 1999 here in VA but it is Art. 230-79(c) for One-Family Dwellings.

Yeppers......I cant remember the last 100A unit we put in. Probably a sub-panel to a detached garage or something but in a house...heck it has been years....I have replaced quite a few...
 
  #9  
Old 06-16-05, 02:52 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Yup. That's what I was looking for. Thanks.
 