30 amp circuit
#2
jarhead786,
You can use 10 AWG for your 30 Amp circuit. Now I can't go without adding you can also use the # 8 AWG as well for a 30A circuit but would be more expensive and overkill since the NEC clearly states for a 30A circuit you can use # 10 AWG.
Let us know how your project works out.
You can use 10 AWG for your 30 Amp circuit. Now I can't go without adding you can also use the # 8 AWG as well for a 30A circuit but would be more expensive and overkill since the NEC clearly states for a 30A circuit you can use # 10 AWG.
Let us know how your project works out.
#4
Great Point Speedy....guess I assumed the poster already had that information and just needed to know the wire size for a 30A circuit. If the issue is length and voltage drop and so on jarhead then check out the online calculator below.
http://www.electrician.com/vd_calculator.html
Simply plug in 120V, 10 AWG, length of the run and amp draw of the circuit in question. Keep the VD below 5 %..
Or basically if the 30A circuit is to supply a item less than 80' away...even at the 30A MAX draw which I doubt will happen but only YOU know that you should be fine....If over 80' you will need to size up your wire to decrease the voltage loss.
http://www.electrician.com/vd_calculator.html
Simply plug in 120V, 10 AWG, length of the run and amp draw of the circuit in question. Keep the VD below 5 %..
Or basically if the 30A circuit is to supply a item less than 80' away...even at the 30A MAX draw which I doubt will happen but only YOU know that you should be fine....If over 80' you will need to size up your wire to decrease the voltage loss.