subpanel, unattach garage.

I been following another threads and just want to clear up a point. unattach garage, no phone lines. 4 wires back to main in conduit, seperate neutral and ground. what about ground rod at garage, yes or no.
 

Last edited by brownbagg; 07-03-05 at 04:09 PM.
Sponsored Links
  #2  
Old 07-03-05, 01:17 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Yes.......
 
  #3  
Old 07-04-05, 12:17 PM
Skapare's Avatar
Member
Join Date: Jun 2004
Location: USA
Posts: 198
Be sure that neutral and ground are NOT bonded in the garage, as this is still a subpanel. The ground rod goes to the grounding wire (green insulation or bare). If it were me, I'd have 2 ground rods, at least 6 feet apart.
 