GFI Breaker Question - 2 Pole or 1 Pole

Reply

  #1  
Old 07-08-05, 06:33 PM
jtfamily
Visiting Guest
Posts: n/a
GFI Breaker Question - 2 Pole or 1 Pole

I am pretty sure I know the answer to this is NO, but I want to know.
I have a 220V outdoor circuit that is not services via GFI breakers and needs to be (its a pool motor).

One 2 pole 20AMP GFI breaker is very expensive
2 - 1 pole 20 AMP GFI breakers is actually cheaper.

Can I use 2 - 1 pole's ?
 
Sponsored Links
  #2  
Old 07-08-05, 07:08 PM
Member
Join Date: Oct 2004
Location: USA
Posts: 719
No.
They will trip.
They need the neutral line
 
  #3  
Old 07-08-05, 07:11 PM
jtfamily
Visiting Guest
Posts: n/a
Thank you.
 
  #4  
Old 07-08-05, 08:15 PM
ampz's Avatar
Member
Join Date: Feb 2004
Location: Philadelphia
Posts: 536
I'd also like to add that any multi-pole circuit must be protected by a breaker that will open all ungrounded conductors {hots} of that circuit,GFCI or standard
 
  #5  
Old 07-08-05, 09:18 PM
Member
Join Date: Nov 2004
Location: CA
Posts: 2,041
Ditto. You may NOT substitute 2 single pole breakers where a double pole breaker is required.
 