EMT recepticle grounding

In attaching a grounding type double outlet in a EMT continuous curcuit, is it necessary to connect a ground wire from the switch box to the grounding screw on the outlet or does the attachment to the metal box constitute a suitable ground?
 
Sponsored Links
  #2  
Old 07-19-05, 03:27 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,342
If the receptacle is rated "self-grounding" then the connection to the metal box is an acceptable ground, provided the box is properly grounded through the conduit or a ground wire. The self-grounding type of receptacles usually grab the mounting screws rather tightly with a copper tab; the screws do not hang loosly like they do in cheaper receptacles.

It is my opinion that good practice dictates attaching a ground wire to both the receptacle and to the metal box "just in case".
 
  #3  
Old 07-19-05, 05:46 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
It depends on the cover. If it is a raised cover the device needs a ground tail no matter what.
The box and cover type determines whether a ground tail is required. It is always good work practice though to use one.
 