service panel clearance question

Reply

  #1  
Old 07-21-05, 12:12 AM
danodiyser
Visiting Guest
Posts: n/a
Question service panel clearance question

Do the accessability clearances of 36w x 30d apply to a sub panel if it is tied into the main panel through a Breaker?
 
Sponsored Links
  #2  
Old 07-21-05, 05:00 AM
HandyRon's Avatar
Member
Join Date: Dec 2001
Location: New York
Posts: 1,365
Clearance applies to any panel, main or sub. You need the width of the panel projected out from the wall 3'.
 
  #3  
Old 07-21-05, 07:37 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
You need the width of the panel projected out from the wall 3'
You need more than the width of the panel, you need 30" projected out 3'.

But I agree that the answer to the original question is "yes".
 
  #4  
Old 07-21-05, 10:15 AM
danodiyser
Visiting Guest
Posts: n/a
thanks

Well that clears that up. Thanks for the help. ,Dano
 