If the rating of a a/c package unit is 24.42 kw, what size disconect should be installed ?
Old 07-21-05, 09:34 AM
Art 440, Part II, Disconnecting means ( A-C equiptment)
440.12, Rating------ " ---- shall be selected on the basis of the name-plate rated-load current, or the Branch-Circuit "selected" current, which ever is greater."
I suggest you refer to the nameplate information which is required to appear on either the motor or the equiptment enclosure.
Good Luck & Enjoy the Experience!!!!!!!!!!!!!11
Old 07-21-05, 11:12 AM
ally68
If you use a nonfused disconnect most of them are rated max 60 amps. If you use a fused one then same as breaker with info from faceplate.