200 Amp service ?

Was adding some branch circuits and noticed my 200 amp service is fed with 4 Ga wires. Is this correct? The main breaker is 2 200 amp brekers ganged together.

4GA wire would only carry 100 amps. Am I really confused as usual or does 200 amp mean both legs added together?

thanks
 
Sponsored Links
  #2  
Old 07-27-05, 06:32 AM
WFO
WFO is offline
Member
Join Date: Feb 2004
Location: usa
Posts: 247
#4 triplex used to be pretty standard for a typical service drop.

The amperage of a breaker is what it will trip at. A 200 amp breaker will trip (in time) around 200 amps. It doesn't matter which leg is carrying the 200 amps....it could be all on one side and none on the other.

They are not precision devices.

Breakers should protect what's below them (i.e.-the load they are looking at), not the wires coming to them. I imagine the wire is sized more to the capacity of your transformer than your breaker.

On the other hand, if you are experiencing excessive dimming of lights when a large appliance cuts in, or you have motors that have trouble starting, this could be causing a voltage drop.
 
  #3  
Old 07-27-05, 07:53 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
The requirements for utility-owned wires are generally less, because such wires are generally outside and pose less of a risk if they should get hot.
 
  #4  
Old 07-27-05, 09:49 AM
scott e.'s Avatar
Member
Join Date: Jun 2003
Location: Anderson, IN
Posts: 412
are the 4 ga wires the service drop or are they the feeders from the weatherhead and meter to the main breaker? I ask this because typically one cannot read the service feeders while looking in the main panel.
 
  #5  
Old 07-27-05, 02:07 PM
montag
Visiting Guest
Posts: n/a
Scott they are the feeders, it is an underground system. They come from the meter box to the service panel.

Thanks
 
  #6  
Old 07-27-05, 02:40 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,541
Are you sure they are 4 gauge and not 4/0 gauge? Actual #4 is a little bigger than a 1/4" diameter whereas #4/0 is about 5/8" diameter.
 
  #7  
Old 07-28-05, 03:26 PM
montag
Visiting Guest
Posts: n/a
Yes they are 4 Ga not 4/0. Thats why I am asking that seems way to small to me, but this was done by a licenced contractor and passed inspection.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes