Dining area circuits

I'm rewiring a 1956 house...

1) If I read (googled excerpts) 210.52 correctly, dining area receptacles can be on the kitchen small appliance circuit(s)? Is this correct?


Thanks!!!
 
Sponsored Links
  #2  
Old 08-01-05, 10:54 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Yes. In fact, they cannot be on any other circuit (except their own circuit).
 
  #3  
Old 08-01-05, 10:55 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Not only can be, must be! You can have as many small-appliance circuits as you want (at least two), but they all must be 20-amp circuits dedicated to kitchen countertop, refrigeration, and dining room receptacles.
 