I have a 40 amp 220v , right now there is a 15 amp oven on it I want to run a 220v 16 amp compressor off it too.

will it work ok, or am I stuck adding another 30 amp breaker for the compressor?
 
Sponsored Links
  #2  
Old 08-03-05, 12:42 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Something is wriong with the statement, "I have a 40 amp 220v , right now there is a 15 amp oven on it," but I will assume you don;t really mean that.

You need a new breaker for your new load.
 
  #3  
Old 08-03-05, 12:51 PM
toolnutz
Visiting Guest
Posts: n/a
ok, but you knew what I meant.

One more question, I have bx to run from the box under the house with the awg 10 for the new 30amp breaker. when I get the garage do I put a juction box where it come out of the house fondation? then run the bx around the ceiling . Or rather than the juction box, keep it solid pipe then connect the bx? I am confused ... my plan is to do the wiring then call the guy to wire it at the box.

Thanks!
 

Last edited by toolnutz; 08-03-05 at 01:08 PM.
  #4  
Old 08-03-05, 05:08 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 5,675
To transition from BX to pipe you need a junction box.
 