finishing basement

I am finishing my basement and purchased 14-2 wire to use for the outlets, and am planning on using a 15A breaker. What is the total amount of receptacles you can install on 1 15A breaker?
 
Sponsored Links
  #2  
Old 08-07-05, 06:22 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
OK, this is a classic topic and I hope it doesn't run into pages of replies.

In the US, residentially, the NEC has NO limit to number of receptacles on a circuit. If the load is known, such as lighting or fixed in place appliances, keep it to 80% of the circuit, or 1440 watts.

The general concensus in the field is typically 8-10 receptacles on a 15 amp circuit.
 
  #3  
Old 08-08-05, 04:02 PM
Member
Thread Starter
Join Date: Mar 2005
Posts: 54
Thanks alot for the insight
 