Wiring GFCI plugs on 12-3 cable

Reply

  #1  
Old 08-16-05, 06:00 AM
robz1330
Visiting Guest
Posts: n/a
Wiring GFCI plugs on 12-3 cable

I am in the process of rewiring the GFCI circuit in my kithchen and I'm having a small problem. I ran the new circuit using 12-3 cable so that 2 plugs could share the black wire and 2 could share the red wire. The first plug on the black circuit is a GFCI plug, with a second 'regular' plug branching off of it. Same goes for the red circuit -- total of 4 plugs altogether. The circuit uses a double-pole 20 amp breaker, with the red wire leading to one and the black to the other.

Both black and red circuits share the white wire, which is pigtailed at each plug and attached to only one of the 'white' screws on each plug.

When I plug a lamp into either of the GFCI plugs, everything works fine. But when I plug the lamp into either of the non-GFCI plugs, the corresponding GFCI plug that is upstream trips.

Anybody know off-hand what the issue is? COuld it be the way the neutral wires are connected?

Thanks in advance for any help!
 
Sponsored Links
  #2  
Old 08-16-05, 06:13 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
You cannot use GFCI receptacles in this manner. With a multi-wire circuit you either need to provide GFCI protection with a GFCI double pole breaker or you need to provide GFCI protection at each receptacle, using only the line side of the devices. Your other option is to switch to using 12-2 after the GFCI receptacles.

The problem you are running into is that the current on the neutral wire does not equal the current on the hot wires. This is how a multi-wire circuit works, and one reason why multi-wire circuits are tricky to use.
 
  #3  
Old 08-16-05, 08:00 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
As Bob says, GFCI and multiwire circuits don't get along well. It's just one of the reasons on my list that I don't really care for multiwire circuits.

You can of course install the double-pole 20-amp 120/240 GFCI breaker, but these are expensive. You can also just buy four GFCI receptacles, connect only the line side of each, and be done with it. Actually, you may only need three depending on exactly how you routed the cable and which outlet is on which hot wire. Or, if the walls are still open, you can split the 12/3 into two 12/2s at the first box, and then you only need two GFCI receptacles.

Bottom line is that you cannot connect a shared neutral to the load side of a GFCI receptacle.
 
  #4  
Old 08-16-05, 10:46 AM
robz1330
Visiting Guest
Posts: n/a
I figured it had something to do with the shared neutral wire. I think I will just buy 2 more GFCI receptacles and be done with it. Thanks for the helpful info!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: