#1
power adapter for 2 wire out of wall
I am installing a microwave/microhood above my range. When the original vent fan above the range was removed I discovered the fan was connected to two wires out of the wall. The new microwave is a standard 3 prong male, and it needs a normal 3 prong felmale outlet to connect to. Can someone help me find where I can get a power adapter with 2 wires on one end and a normal 3 prong female socket on the other.
Also, I'm assuming the red wire is "hot" and the white wire is ground.
Also, I'm assuming the red wire is "hot" and the white wire is ground.
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NEVER EVER MAKE AN ASSUMPTION WHEN WORKING WITH ELECTRICITY! Electricity can kill. Making an assumption can get you killed.
Neither wire is ground. One wire is grounded, but it is not ground, it is a return.
You need to rewire. Do not use the existing wire. You need to have a dedicated circuit run for this microwave range hood. A proper ground is a necessity.
Neither wire is ground. One wire is grounded, but it is not ground, it is a return.
You need to rewire. Do not use the existing wire. You need to have a dedicated circuit run for this microwave range hood. A proper ground is a necessity.
#4
Microwave range hoods require a dedicated, grounded circuit. You need to run a new circuit just for this microwave, and it must be properly grounded. This requirement is usually on the first page of the installation instructions which will also specify if this circuit must be 15A or 20A. I bet it's 20.