Another Basic Question on Breakers

I have read several times that #14 wire is for a 15 amp breaker and #12 wire is for a 20 amp breaker. Is it code compliant to use #12 wire with 15 amp breakers. I already have several of these in the panel box (used panel box) but I am doing all my wiring with #12 wire. Thanks in advance
 
Sponsored Links
  #2  
Old 09-12-05, 07:18 AM
Member
Join Date: Jul 2005
Location: Central Indiana
Posts: 192
Received 0 Votes on 0 Posts
Yes. 12 AWG is protected by a 15 Amp breaker.
 
  #3  
Old 09-12-05, 07:27 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Yes, you can protect 12 gage wire with a 15 amp breaker. But why?

You would be wasting capacity by limiting these circuits to 15 amps and wasting money on more expensive 12 gage wire.

My suggestion is to use 20 amp breakers on these circuits, unless you have a specific and compelling reason to use 15 amp breakers.
 
  #4  
Old 09-12-05, 08:18 AM
Member
Thread Starter
Join Date: Aug 2005
Posts: 145
Received 0 Votes on 0 Posts
Another Basic Question on Breakers

I have no reason to use 15 amp other than the fact I already some in the box. They are relative inexpensive, so it would be better just to replace the 15's with 20's Thanks
 
  #5  
Old 09-12-05, 08:42 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
If this were my project, I would install 20 amp breakers. You will appreciate the extra capacity of the circuits and it is easier to make change now, rather than later.

Another consideration and reason to use 20 amp breakers is to avoid confusion later on. Someone else (or even yourself later on) may want or need to work on or extend the circuit. Seeing a 15 amp breaker they may think they need 14 gage wire, only to find 12 gage wire once they remove the covers.

If you do stay with the 15 amp breakers, I recommend making a note on the panel that the circuit is all 12 gage wire, so that someone will know this in the future and not be surprised.
 
  #6  
Old 09-12-05, 10:15 AM
Member
Thread Starter
Join Date: Aug 2005
Posts: 145
Received 0 Votes on 0 Posts
Another Basic Question on Breakers

Thanks Bob
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: