Gfci

I want to re-wire a 20A circuit with a gfci but I 4wire output to a three wire circuit, by elimanating the neutrel. can I do this without causing problems with the gfci? Should the gruond ang neutrel tie together at the service panel?
 
Sponsored Links
  #2  
Old 09-12-05, 10:03 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Try your post again, or go back end edit it. I'm not sure what you are trying to ask.
 
  #3  
Old 09-12-05, 11:40 AM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
When using a GFCI receptacle on a multiwire circuit, the cardinal rule is that you may not attach a shared neutral to the load side of a GFCI. So that means that you can either (1) not use the load side of the GFCI, or (2) split the neutral so that it no longer shared. Of course you always have the (expensive) option of using a 120/240 double-pole GFCI breaker on a multiwire circuit.
 