Hi! I need help in the conversion of a 240v outlet to an extension of 120v outlet.

I thought of using the neutral / grounded wire and one of the hot wires to obtain the 120v. Yet my question is -can I connect the grounding to the same neutral return line? or should I connect the grounding to a near copper water pipe? [this second solution seems more elegant, yet it is about the same since the 240v neutral wire is also connected to the water supply further up].

Any comments? advice? it would be greatly appreciate it.
 
Sponsored Links
  #2  
Old 09-20-05, 02:32 PM
Member
Join Date: Jan 2004
Location: Oregon
Posts: 1,219
Received 0 Votes on 0 Posts
You cannot use either of the approaches that you suggest.

Please describe the 240V line that you are converting; there may be additional options. What sort of cable are the wires in, or are the wires in conduit?

If you need to run a new ground wire, you must run the wire back to your panel or to the grounding electrode conductor; you can't simply use a water pipe.

Your electrical system is _bonded_ to your water system to protect you from shocks from the water system, and also to use underground water pipe as a grounding electrode. But this doesn't mean that the water pipes are considered proper equipment grounding conductors. The _grounded_ conductor (neutral) is connected to the electrical ground bus at the panel, however it is a current carrying conductor. An equipment grounding conductor must not carry current in normal operation.

-Jon
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: