Question sorry to hijack the thread

SO my house buyers inspection called my panel "hazardous" and noted "14 gauge wiring in use on 15 amp circuit present in box". he also noted "over fused wiring"
so is this guy calling hazardous the overfused wiring or the 14ga in 15A circuit?
if i understand th previous threads, 14ga in a 15A circuit is OK, right?
 
Sponsored Links
  #2  
Old 09-21-05, 05:28 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
14 gage wiring is correct for 15 amp circuits.

Find out what is/was considered hazardous. Perhaps there is something else he or she doesn't like.
 
  #3  
Old 09-21-05, 10:53 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Are we talking about aluminum or copper wire? #14 is only okay if the wire is copper.
 
  #4  
Old 09-21-05, 12:39 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Is the hazard because of the panel itself, such as Zinsco or Federal Pacific (FPE) brand?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: