subpanel wire size?
Old 09-27-05, 02:04 PM
myvalk
subpanel wire size?
put up an addition attached to the house. have an 8 breaker sub panel in there. 5 - 15 amp bkrs. for lites and recepticals and a smoke detector. and 2 - 20 amp bkrs for electric heat. and 1 - 20 amp for a spare.
question is ...what size cable to run to power this sub panel?
#4 ? #6? and what size breaker for that cable from my main box.?
thanx in advance
Old 09-27-05, 02:35 PM
How many square feet are in the addition?
Is there a bathroom in the addition?
What other rooms are in the addition?
Is the electric heat 120-volt or 240-volt? How many watts?How far is the subpanel from the main panel (measured along the cable)?
I'm going to guess that the answer is 6/3 cable and a 60-amp double-pole breaker, but the answers to the above questions will help ensure that this is the right answer.
Old 09-27-05, 04:13 PM
myvalk
ok... one big room no bath or kitchen.. just as i said lites and outlets.
one mistake was the heat. two branches, 220v each 20 amp brkr. 3500 watts each so its four 20's for the heat, not two. and one 20 for a spare.
cable run is 20 feet.
room is 24 x 20 feet
i think that does it.... thanx
Old 09-27-05, 06:37 PM
The room is 480 square feet. That will require about 500 watts of lighting. You'll have 7000 watts of heating. You'll need at least 8 receptacles, and it's normal to allocate about 180 watts for each, so that's about another 1500 watts. That adds up to 9000 watts. To allow flexibility and expansion, let's double the non-heating load. That gives us 11000 watts. That's about 45 amps. So I'll stick with my recommendation for 6/3 from a 60-amp breaker.
Old 09-28-05, 02:07 AM
myvalk
thank you... thats what i'll do.