Securing Wires into Sub

Do I need to secure the cables coming into the sub panel and going out?

The panel is surface mounted and I have 1" pvc coming in and 3/4" Armored going out to a compressor.

Also, Will this need to be done in the main panel? It does not appear any of the other cables are secured going into the house.
 
Sponsored Links
  #2  
Old 10-06-05, 08:26 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,335
Wires that come in through conduit, flex, or AC do not need to be secured because the conduit will already be fastened to the box. Cables like Romex (NM) need to be secured with a screw-in cable clamp when they enter the box.
 
  #3  
Old 10-06-05, 09:28 AM
bigblock
Visiting Guest
Posts: n/a
Cool, I did it correctly then.....

Thanks for the tip....This forum is great!
 