question about adding a 220 circuit

Im going to wire a 220v 20a circuit in my garage for a air compressor. The wall im putting it on has no 110 outlets, so i want to add a 110 outlet also. My question is, can i run 12/3 and run a 110 outlet off the same circuit, or do i need to run 2 seperate wires? I know i can, but not knowing the codes, im not sure if it would be ok code wise. I was going to install them in the same box, what is the proper way to do this? thanks
 
Sponsored Links
  #2  
Old 10-08-05, 04:56 PM
ampz's Avatar
Member
Join Date: Feb 2004
Location: Philadelphia
Posts: 536
No you cannot do this.The 220 line must be a dedicated circuit on its own 2 pole breaker.The 110 receptacle can share a circuit with other receptacles.You can use the same box but there must enough space in the box for the receptacles,wires & there must be a non-conductive barrier between the two devices.I would use 2 seaparate boxes
 
  #3  
Old 10-08-05, 08:33 PM
packy
Visiting Guest
Posts: n/a
ok, thats what i needed to know, thanks
 