new load center; fire rated wall Q.

Reply

  #1  
Old 10-13-05, 12:48 PM
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 1,153
new load center; fire rated wall Q.

I'm getting built a new, attached garage. There is to be a 1 hr fire rated wall adjacent to living areas, as I read the Code. In one of these walls, I intend to place a flush 200amp load center. Clearly, the sq. in. of a load center will exceed the max spec of an opening. The wall, will be a 6" stud framed, 5/8" drywall. What are my options to preserve the fire rating of this wall?
thanks!
 
Sponsored Links
  #2  
Old 10-13-05, 12:51 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Surface mount the box?
 
  #3  
Old 10-13-05, 01:09 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
... or put the panel in a different wall.

Or if flush mount is important, build a second wall in front of the first.

You also might ask your inspector if it's okay to put two layers of 5/8" Type X drywall on the interior. That might provide the fire rating so that you can flush mount the panel on the garage side.
 
  #4  
Old 10-13-05, 01:13 PM
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 1,153
I could surface mount this 42 ckt box on drywall, but am aiming for something a bit more elegant. I've got a 1 1/2" main feed coming up from a poured slab that i'd rather keep inside the wall. Also, working with NM cable and clamps out the backside of the box thru drywall isn't appealing. I have seen some pourable wall fill that is used in fire rated walls. Is that ever used in residences?
 
  #5  
Old 10-13-05, 01:38 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,342
Unlike electrical code, building code tends to vary a lot by region of the country so I think the best resource you will have is your local building department.

I would consider surface mounting the box and install a number of 1/2" or 3/4" EMT conduits from the box up to the attic to run your Romex into the box. That way you will not have a bunch of exposed Romex above the box, and you can paint the conduit to match the wall for a clean "industrial" look.
 
  #6  
Old 10-13-05, 03:06 PM
TomZ1's Avatar
Member
Join Date: Sep 2003
Location: New Hampshire
Posts: 174
Assuming this is a single-family home...unless you have a local code/ordinance, generally the model fire and building codes don't actually require a 1-hour rated wall between the garage and living space. They normally specify a minimum of 1/2-inch drywall and a 20-minute steel or 1-3/4 inch thick solid wood door. Similar but not actually 1-hour fire rated construction.

I would check with your inspector and see if you can put the required drywall behind the panel. Or... the surface mount option is still there.

tjz
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'