Feed Single pole switch from 3-way

I have 12-2 coming into my bath on a 20 amp circuit. I have power coming into a 3-way switch then 12-3 running from the switch to light to switch. Can I tap into the 3-way switch at the end of the run and add a receptacle that will always be on?

Thanks in advance
 
Sponsored Links
  #2  
Old 10-14-05, 01:59 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
No, not without replacing the wire from the light to the second switch. The second switch has no neutral wire.
 
  #3  
Old 10-14-05, 02:38 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 5,680
You can't even do with a new cable from the light. You need to go all the way back to the first switch where the power comes in.
 
  #4  
Old 10-14-05, 02:58 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Thanks for the correction Joe. My mind must have been on the fritz.
 