nEW CIRCUIT

I'm running a circuit from my main panel to my shed about 130 ft away ...I ran 10 gauge wire from a pull box in my basement to a box in the shed...my question is con I run 12 gauge from my panel to the pull box and splice the 10 and 12 together or do i need to run 10 from the panel to the pull box?...Thanks
 
Sponsored Links
  #2  
Old 11-04-05, 10:57 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
If you are protecting this circuit with a 20 amp breaker then you can run 12 gage wire.
 
  #3  
Old 11-04-05, 08:15 PM
New Member
Thread Starter
Join Date: Mar 2003
Location: PA
Posts: 406
Received 0 Votes on 0 Posts
Thanks...12 from the panel to pull box...10 150 to shed...12 to recpt. and light... right...
 
  #4  
Old 11-05-05, 05:22 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Frankly I would run 10 gage all the way to the shed, and I would not have made a junction where the cable exits the house, but you certainly can.

What type wire are you using? In conduit? GFCI protected?
 
  #5  
Old 11-05-05, 09:37 AM
New Member
Thread Starter
Join Date: Mar 2003
Location: PA
Posts: 406
Received 0 Votes on 0 Posts
10 gauge stranded in pvc.....I can run 10 from the panel to the juction box...If it wasn't such a long run I would have run 12 gauge...Thanks
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: