Wiring close to roof

Reply

  #1  
Old 11-07-05, 09:42 AM
silverfox1208
Visiting Guest
Posts: n/a
Wiring close to roof

Are there any restrictions on electrical wiring running right under the roof.
ie, over game room in v of roof or back to inside main panel.

Thanks
 
Sponsored Links
  #2  
Old 11-07-05, 11:32 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,342
I think you're talking about wiring in an attic? If the wiring is close enough the the roof where it could be hit by roofing nails, then it is too close. Along the side of a truss should be okay. Anywhere in the attic that is subject to potential foot traffic or storage, the wiring should be protected by a substantial running board like a 2x4.
 