grounding rod placement for 200amp panel

Reply

  #1  
Old 11-14-05, 10:44 AM
Member
Thread Starter
Join Date: Nov 2005
Posts: 12
grounding rod placement for 200amp panel

I am installing a 200 amp electrical box on a barn that I have built. It is 100ft from the nearest electrical pole where the power company will make the connection. I have been told by someone that I need 3, 10ft grounding rods connected with copper grounding wire. I don't know where to place them in the ground though. I assume one should be pretty much under the panel but how far away should the other 2 rods be? Any help would be greatly appreciated.
 
Sponsored Links
  #2  
Old 11-14-05, 11:21 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,337
They should be at least 6 feet apart.
 
  #3  
Old 11-14-05, 11:52 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Depends on who "someone" is, and on what the codes are where you are, and on how your inspector feels today.

But the "normal" way would only require two (not three) rods 8 feet (not 10 feet) in length, driven vertically until the top is flush or below ground, six or more feet apart.

There are other grounding requirements too, but you only asked about grounding rods, so that's all we've covered so far. Is there a metal water pipe serving this barn?
 
  #4  
Old 11-14-05, 12:16 PM
Member
Join Date: Jul 2005
Location: Central Indiana
Posts: 190
Will there be any livestock or other animals residing in this barn? If so, the NEC may have a few special requirements to follow such as an equipotential plane to be installed.
 