GFI Breaker Change

Currently have 15amp two pole GFI breaker in panel that trips often. Want to change to 20 or 30 amp to support current loads. Should this be a problem?

Thanks,
bigpigzeb
 
Sponsored Links
  #2  
Old 11-19-05, 07:34 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Yup. BIG problem!

You cannot simply put in a larger breaker. The breaker must be sized accordingly to the circuit conductors.

Unless ALL the wiring in this circuit is larger than #14 you CANNOT change the breaker for a higher rated one.
 
  #3  
Old 11-19-05, 07:34 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Are you sure it is tripping from overcurrent? Could it be a ground fault trip?
What is the load?
 