Double pole Gfci Question

Reply

  #1  
Old 11-22-05, 10:31 AM
jericoriver
Visiting Guest
Posts: n/a
Double pole Gfci Question

Can two single pole gfci's be used without causing a problem? Instead of a double pole. (I have the two singles and will have to wait on the double pole)
 
Sponsored Links
  #2  
Old 11-22-05, 10:32 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Not on a multi wire circuit. If you have a multi wire circuit then you must use a double pole GFCI breaker to provide GFCI protection at the breaker.
 
  #3  
Old 11-22-05, 10:38 AM
jericoriver
Visiting Guest
Posts: n/a
I would be using it to power a boat lift. #12 wire and nothing else. If I lock the 2 together(trip handles) would it then be O K or would there be a problem with the G F part.Thanks
 
  #4  
Old 11-22-05, 10:51 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
This will not work if it is a multiwire circuit. It also will not work if it is a 240 volt circuit.
 