need code # from 2002 book

does anyone know where in the code book that it says 120volt and 277volt that you would need a divider in junction box?
 
Sponsored Links
  #2  
Old 11-28-05, 04:27 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
There is no such requirement.
 
  #3  
Old 11-28-05, 04:48 PM
JIGGA WATT
Visiting Guest
Posts: n/a
So It Is Also Alright For The 120v And 277v To Be Ran In The Same Raceway
 
  #4  
Old 11-28-05, 05:05 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Yup. As long as all the conductors have insulation rating to at least the highest voltage present.
NEC ~ 300.3(C)
 
  #5  
Old 11-28-05, 06:51 PM
Member
Join Date: Jan 2004
Location: Oregon
Posts: 1,219
See 404.8(B). If you exceed 300V between adjacent devices, then you are required to have a barrier. Normally this comes into play with 277V switches from different phases, which have 480V between them.

With mixed 480Y/277 wiring and 208Y/120 wiring, you can have anything from about 150V to 400V between a random 277V hot and a random 120V hot, and about 2/3 of the time you will exceed 300V and a barrier would be required.

Note that this barrier is between the switches only, and is not required in the raceway.

I'd suggest also noting 200.6(D) identification of the grounded conductor (neutral)

-Jon
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes