Hot Outlet
Old 12-02-05, 09:50 AM
lucycart
Hot Outlet
I have an outlet in my enclosed patio that is getting hot. I had a space heater plugged into it and there is an odor from it. Do I need to just replace the outlet or rewire? It is the second outlet in a chain of 3. Thank you for any information.
lucycart
Old 12-02-05, 09:58 AM
A space heater is a very large load. Probably the largest cord-and-plug connected load in your whole house. It should not be run unattended, and is not a good long-term solution for heating this room. And should not be used for more than an hour or two at a time.
I recommend that you replace all receptacles in the chain with high-quality commercial-grade receptacles, and use the side screws (not the holes in the back) to connect the wires. You need the best connections you can get.
Old 12-02-05, 10:06 AM
Replace the receptacle, using "device-leads" best done with standed THHN wire for flexibility.The objective is to avoid " in-and-out" connections on the device terminals. I would invest in "crimping" pliers and use crimp-type lugs for a "solid" connection at the terminals-- a loose terminal connection may be the cause of the heating problem.
Twist the 2 Black/White wires together,and wire-nut 6" device-leads to the Black/White wires.With this connection, a defective device-connection will not open the circuit.
I hope you don't have Aluminum wiring.
Good Luck, & Learn & Enjoy from the Experience!!!!!!!