no neutral


  #1  
Old 12-03-05, 09:08 AM
T
New Member
Thread Starter
Join Date: Mar 2003
Location: PA
Posts: 403
Upvotes: 0
Received 0 Upvotes on 0 Posts
no neutral

I was looking inside my panel (200 amp)...and noticed a 30 amp breaker that supply's my air ccondition unit...connected to the breaker was a hot and a neutral taped black...doesn't this circuit need a neutral?.....it is supplying the disconnect outside to the airconditioner...Thanks (I thought all circuits need a return (neutral))
 
  #2  
Old 12-03-05, 09:14 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
Straight 240 volt circuits like an air conditioner, water heater or baseboard heat do not need a neutral.
 
  #3  
Old 12-03-05, 09:14 AM
MXSparx
Visiting Guest
Posts: n/a
Originally Posted by ThomasB
doesn't this circuit need a neutral?
no.
2 hots and a ground is all it needs.
Sometimes 220 volt circuits will have a neutral (not always) for lights and clocks and the like.
 
  #4  
Old 12-03-05, 09:16 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
No, all circuits do not need a neutral wire. All circuits do need a return wire, but they all do not need a neutral.

The term neutral is used because the wire is electrically neutral to the two incoming 120 volt wires of your service. The term is return is also used for this wire on 120 volt circuits because it is the return path for the current.

240 volt circuits in the US are different. The voltage between the two hot lines entering your house is 240 volts. Devices that use only 240 volts do not need a neutral. The return path for the current on each wire is the other wire. No current flows on the neutral wire.

Devices like air conditioners, baseboard heaters, water heaters and such are only 240 volts and don;t need a neutral.

Other devices are actually both 240 and 120 volts. These include electric dryers and ranges. The 120 volts is needed to power light bulbs, the dryer tumbler motor and electronic controls. The 240 volts is needed for the heating element.

So your air conditioner is a 240 volt device. It gets its power on the two wires you have identified, the black wire and the white wire. The white wire is properly re-identified as a hot wire. This is allowed since the wire is part of a cable assembly. You should not refer to the white wire as a neutral, since it is not. In fact, you should not refer to any white wire as a neutral, unless it is acting as a neutral.
 
 