can i share garage with hall way recept?

OK, i've got the 2005 NEC in front of me and I can't find any reference to a violation of shared circuits except for laundry and bath. (210.11C) I'm i missing something?
 
Sponsored Links
  #2  
Old 12-14-05, 06:30 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
The NEC is not the easiest thing to read.

If you are asking if a garage receptacle can be shared with a hallway receptacle, the answer is yes.

But before you proceed, consider what you pl;an to use the receptacle for and what is already on the circuit. Remember that a garage receptacle needs to be GFCI protected. A hallway receptacle does not, but can be.
 
  #3  
Old 12-14-05, 07:10 AM
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 1,152
great, thanks!
 