low voltage


  #1  
Old 01-06-06, 04:15 PM
M
Member
Thread Starter
Join Date: Jan 2006
Location: indiana
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
low voltage

I am new heree but i have found this site very informative and interesting, keep up the good work.

I've started having a problem with one part of the house has good power but another part has low current(83 volts). In the the fuse box i can take out the fuse where i have low voltage and a light gets brighter, also when unhooking a wire from my water heater the light will go out. All fuses are good.
Is this a case of losing one phase coming into the house?
 
  #2  
Old 01-06-06, 04:34 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
I had a similar incident occur to me in an older neighborhood. I finally tested each phase to ground and determined one was actually only 69 volts. There was nothing else I could do but call the power company. After fiddling and scratching, they deterimined it was a bad transformer. They changed it out and we had proper voltage thereafter. Not sure if that will be the case with you, but just thought I'd throw it out.
 
  #3  
Old 01-06-06, 04:35 PM
C
Member
Join Date: Apr 2004
Location: Ontario Canada
Posts: 1,694
Upvotes: 0
Received 0 Upvotes on 0 Posts
Probably. Or a bad neutral.
 
  #4  
Old 01-06-06, 04:40 PM
M
Member
Thread Starter
Join Date: Jan 2006
Location: indiana
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
low voltage

thanks a lot
 
  #5  
Old 01-06-06, 05:09 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
Almost definitely a bad neutral somewhere. Start by calling your POCO immediately!
 
  #6  
Old 01-06-06, 05:53 PM
J
Member
Join Date: Sep 2000
Location: United States
Posts: 17,733
Upvotes: 0
Received 1 Upvote on 1 Post
If you haven't called your power company, do so now. Not ten minutes from now, but now. Dragging your feet on doing this would be very ill-advised.
 
  #7  
Old 01-06-06, 07:31 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
You are missing one half of your incoming power. Half of your panel is being fed through your water heater circuit, which accounts for the funny voltages.

As has already been told, call your power company immediately. It doesn't matter what time you read these, call right away.

Then go and shut off your water heater breaker and any other 240 volt breaker you have. better yet, turn off your main breaker, but since you probably won;t do that, at least turn off your 240 volt breakers.

This is nothing to ask questions about or wait on. Call right away!
 
  #8  
Old 01-09-06, 03:47 PM
M
Member
Thread Starter
Join Date: Jan 2006
Location: indiana
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
low voltage

Thanks for all the help, the poco was called, it was a bad meter base, one lug was bad all is well now.
and thanks again for all the help
 
  #9  
Old 01-09-06, 04:57 PM
frhrwa's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2005
Location: Deer Park WA
Posts: 489
Upvotes: 0
Received 0 Upvotes on 0 Posts
a friend of mine in the San Juan Islands had the same type problem.. and, when they would try to take a bath or shower, they'd get shocked... turned out to be "no neutral"... I'd definately get the power company out to look at it pronto haste....
 
 