Installing a 20 amp wall oven on a 30 amp ckt.

Hi all,
I am replacing a wall oven that required and is wired on a 30 amp circuit (the box has two 15 amp breakers supplying the circuit). The new oven requires 20 amps....what is the best way to proceed with installing the new oven? Do I need to replace the two 15 amp breakers, the entire circuit, etc...?

Thanks,
TD
 
Sponsored Links
  #2  
Old 01-07-06, 10:25 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Your old oven required 15 amps, not 30. It needed 15 amps at 240 volts.

If your new oven needs 20 amps at 240 volts then you will need a 20 amp circuit. if the existing wiring can handle 20 amps (12 gage copper) then you can replace the breaker with a 20 amp breaker. If the wiring cannot handle 20 amps then you will need to run new wire.

If your new oven needs 20 amps at 120 volts (not likely) then you would need to convert the circuit over to a 120 volt circuit. You would have the same wire size issues, where you might need new wiring for the higher current flow.
 
  #3  
Old 01-07-06, 10:32 AM
Member
Thread Starter
Join Date: Jan 2006
Posts: 2
Received 0 Votes on 0 Posts
That's interesting. The technical specs call for 30 amps, and the two 15 amp breakers are tied together in the box. Can you give me some additional info?

Thanks,
TD
 
  #4  
Old 01-07-06, 10:40 AM
Join Date: Jan 2006
Posts: 50
Received 0 Votes on 0 Posts
15 and 15 in this case doesnt equal 30 its 15 amps on 1 wire connected to it and 15 amps on the other wire connected to it and yes they seem to be connected together but they are seperate the thing is, if one side sees fault then both open the circuit
now with this in mind do yourself a favor and call a professional
 
  #5  
Old 01-07-06, 01:08 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 2 Votes on 2 Posts
IN a 240 volt situation, you are drawing your voltage from both buss bars on your circuit breaker panel, through the double breaker. The amperage rating on the breakers are "total" amperage. You don't add them together. So if they say 15 amps, the circuit is 15 amps. Check the size wiring to see if you can use a larger breaker, but please don't apply a larger breaker than the wire can handle. To do so would make the wiring your fuse, and the breaker would likely not trip until after the wires burned in two.
 
  #6  
Old 01-07-06, 06:00 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
If each of the four tires on your car is traveling at 25 MPH, is the car going 100 MPH? Of course not. The 25 MPH of each tire is the same 25 MPH, so you cannot add them.

It's the same way with a double-pole breaker on a 240-volt circuit. The 15-amps on the two breakers is the same 15 amps.
 
  #7  
Old 01-08-06, 11:31 AM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
What is the wattage rating of this appliance?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: