200 amp feeder wire

Reply

  #1  
Old 01-13-06, 10:19 AM
P
Member
Thread Starter
Join Date: Jan 2006
Posts: 2
Received 0 Votes on 0 Posts
200 amp feeder wire

I am installing a new 200a service on my pole 150 feet from my old house. The meter box will have a disconnect and a feeder breaker and I am running the feeder wiring through 2 in. conduit to the subpanel in the house. My local electrician says use AL (cost) while another says CU (likes it better). My Question, What is the mininum size and recommended size for both types. The service is moderately oversized as I use propane for water heat and dryer, but I have garage/ shop and barn on another sub, and I am adding 800 sq. feet to house.
 
Sponsored Links
  #2  
Old 01-13-06, 11:56 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
If your inspector will allow the use of Table 310.15(B)(6) for sizing the subpanel feeder, then 2/0 copper THWN or 4/0 aluminum THWN is correct. If not, you need 3/0 copper THWN or 250 kcmil aluminum THWN. If you pull a ground, it needs to be #4 copper or #2 aluminum.

Al wire is cheaper, but takes more work to install correctly because of the larger size and the need for de-oxidizing connections. AL wire can be problematic in direct-burial appliactions, but you're using conduit. Sometimes, Al terminations will need to be re-tightened after a few weeks of use. If installed correctly, Al wire is considered safe for service feeders.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: