ground stud in load center
In my new load center there is a copper lug electrically connected to the grounding bus bar that is sitting next to the neutral bus bar. It looks like something you might connect a spring loaded clamp to as a test point. I have no idea why it is in there as this is not a meter panel where the neutral would be grounded. The neutral is electrically isolated on the panel. As far as I'm concerned the ground shouldn't be anywhere near the neutral in this subpanel. But I'm sure it has some function or it wouldn't be there. Can anyone clue me in?
Steve
Steve
#2
Are you talking about a new load panel that you just bought or something that has been installed?
Is it connecting the grounding busbar, the panel and the neutral busbar?
The grounding and neutral busbars can be joined in the service panel off of the meter, but not in a subpanel.
Is it connecting the grounding busbar, the panel and the neutral busbar?
The grounding and neutral busbars can be joined in the service panel off of the meter, but not in a subpanel.
#4
Member
Thread Starter
Join Date: Dec 2005
Location: Ventura CA
Posts: 53
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Grounding Strap! I tried fitting it into the neutral bar and it screws right back into the panel. I'm removing it because this is a subpanel and I don't need or want the neutral bar grounded.
Thanks!
Steve
Thanks!
Steve