Adding Garage Panel to House Service

Reply

  #1  
Old 02-11-06, 11:06 AM
Member
Thread Starter
Join Date: Feb 2006
Posts: 3
Adding Garage Panel to House Service

What is the most economical way to add a garage electrical service to my house service. I have a 100 amp panel in the house and a 100 amp breaker @ the service outside feeding the panel in the house. I would like to be able to use a small air compressor and welder from time to time.
 

Last edited by mdb60575; 02-12-06 at 05:56 AM.
Sponsored Links
  #2  
Old 02-11-06, 11:12 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Something doesn't sound right here. If the breaker already feeds the house, you shouldn't be trying to feed the garage off the same breaker.
 
  #3  
Old 02-11-06, 12:19 PM
Member
Thread Starter
Join Date: Feb 2006
Posts: 3
Adding Garage Panel to House Service

What do you suggest.
 
  #4  
Old 02-11-06, 01:45 PM
Member
Join Date: Apr 2004
Location: Ontario Canada
Posts: 1,767
Install another breaker beside it, or a breaker in your house planel.
 
  #5  
Old 02-11-06, 03:12 PM
Member
Thread Starter
Join Date: Feb 2006
Posts: 3
Adding Garage Panel to House Servic

If I put another breaker to the side of the existlng 100 amp breaker, will I have to up the utility feed size. Assuming I have a 100 amp service and the new breaker is 100 amp . Or how large of a breaker could I install this way without having to change the service size.
 
  #6  
Old 02-11-06, 04:25 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 695
Service conductors are sized by calculation!

The size of your service conductors is determined by the calculated load they will serve. A single breaker must be matched to the size of the service conductors but two to six breakers must sum to a total that equals or exceeds the ampacity of the service conductors. It is also acceptable on residential property to run a separate set of service entry conductors to an outbuilding from the load side of a single meter. You would have to use multi conductor lugs or patent taps to run the second set of conductors.
 