NEC Code for range wiring

Were are in the process of installing a new duel fuel range. The information the the stove states that it has a 3.6KW / 240 rating and that 20amp 12 guage wire is okay. To be safe I ran 10/3 and was going to put it on a 30 amp 240 breaker. I was told that even though this maybe true, code requires that 8/3 needs to be run for ranges regardless if the stove draws that high of amps. Is this true? Idaho follow NEC.

Thanks,
Clay
 
Sponsored Links
  #2  
Old 02-22-06, 12:05 PM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
The requirement for conductors with an minimum ampacity of 40 applies only to ranges rated at 8-1/4 Kw or more.

Art210.19 (A) (3)
 
  #3  
Old 02-22-06, 12:21 PM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
Received 0 Votes on 0 Posts
Originally Posted by store934
it has a 3.6KW / 240 rating and that 20amp 12 gauge wire is okay. To be safe I ran 10/3
Okay.

> and was going to put it on a 30 amp 240 breaker.
You need to use a 20A double-pole breaker.
 
  #4  
Old 02-22-06, 12:38 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 43 Votes on 41 Posts
You must follow the Manufacturers' instructions to be compliant with the NEC; install a 20A breaker if the installation manual says to use a 20A.
 
  #5  
Old 02-22-06, 02:12 PM
S
Member
Thread Starter
Join Date: Feb 2006
Posts: 8
Received 0 Votes on 0 Posts
Okay, thanks for the help!
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: