I live in an old house (1876) that has a 100 amp panel. My dryer circuit has a 40 amp breaker. I have used it for quite some time. Recently I saw that my dryer is supposed to have a 30 amp supply. Should I replace my breaker? Can I just swap out the 40 for the 30? My supply cable runs into a 3 prong outlet.
 
Sponsored Links
  #2  
Old 03-01-06, 04:43 PM
hornetd's Avatar
Member
Join Date: Aug 2001
Location: Maryland
Posts: 695
Check The Wire Size!

If the wire to that outlet is #10 CU or #8 Al or larger then you can just change out the breaker. Larger wire is fine but smaller than that and you will have to run new wire. I suspect that if it were smaller than that you would have made the aquaintance of your nearest fire stations crew by now.
 
  #3  
Old 03-01-06, 04:57 PM
Member
Thread Starter
Join Date: Feb 2006
Posts: 6
Thanks Tom! I appreciate the info. Not sure of the size. It is braided cable about the diameter of a thn pencil.
 
  #4  
Old 03-01-06, 05:31 PM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
> It is braided cable about the diameter of a thin pencil
Sounds like #8 stranded.

That is large enough for the breaker. But the breaker is oversized for a clothes dryer.
Presumably you have a 30A receptacle.

Yes, you should have a 30A breaker. Is having a 40A likely to result in a visit from the fire dept? I don't see why.
 