EGC size

200 amp main panel feeding a 100 amp sub panel with a 100 amp feeder breaker and #3 AWG current carrying feeder conductors. What size EGC do I use? Thanks.
 
Sponsored Links
  #2  
Old 03-03-06, 09:12 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
#8 copper is the minimum.
 