200amp Upgrade
Old 03-09-06, 04:47 PM
200amp Upgrade
My friend had a service upgrade from 150 to 200amps and the electrician said he had a Murray 40 circuit breaker panel. The schematic on the door shows up to 40 circuits but I only count 30 knockouts. Am I missing something?
Old 03-09-06, 04:55 PM
It probably will allow 10 twin breakers. Those 10 twins would be 20 circuits to go along with the other 20 circuits making 40.
Old 03-09-06, 04:58 PM
Speedy Petey's Avatar
That is a 30/40 panel. 30 space, 40 "circuit". With regard to panels and breakers each "pole" of a breaker is considered a "circuit".
For the panel in question, it will accept twins in the bottom 10 spaces. A twin is also considerd two circuits.
408.35 Number of Overcurrent Devices on One Panelboard
Not more than 42 overcurrent devices (other than those provided for in the mains) of a lighting and appliance branch-circuit panelboard shall be installed in any one cabinet or cutout box.
A lighting and appliance branch-circuit panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and approved.
For the purposes of this article, a 2-pole circuit breaker shall be considered two overcurrent devices; a 3-pole circuit breaker shall be considered three overcurrent devices.
Old 03-10-06, 03:17 AM
Thank you guys I understand now but why double up? Why didn't the electrical contractor just put in a full 40 breaker panel? Does it take up too much space? Thanks
Old 03-10-06, 08:03 AM
For the same reason any contractor does anything: cost.
Old 03-10-06, 09:28 AM
It turned out very good with power also run up to the attic for the central air that will be installed for the second floor zone next week. Thanks