20A vs 15A for general use circuits...?
Quick question. For general use circuits that feed receptacles in, say, bedrooms or offices, is it typical to install 15A circuits or 20A circuits. Of course in areas where code dictates 20A circuits, dedicated or shared, those would be 20A, but for other rooms, let's say receptacles in a dining room, family room, etc, are 15A circuits the norm?
Thanks.
Thanks.
Dining room receptacles must be 20 amp, and are subject to the same rules as kitchen counter top receptacles.
In other rooms the choice is yours. However, I would never install a circuit serving receptacles as anything but 20 amps. The cost is only slightly higher for 12 gage wire and you get 33 percent more power. To me it's a no brainer.
thanks guys. just checking. I was planning on the 20A but I saw in my reference book that a lot of these circuits are stated as 15A, but I'm sure this is the minimum rather than the norm.
Originally Posted by bolide
(Other than where 20A receptacles are required, it is fine to use 15A receptacles on a 20A circuit.)
In the US the dining room receptacles need to be on the small appliance circuits. This is because it is conceivable that you might plug appliances into these receptacles for serving, perhaps in a buffet setup.
In the US it is legal to use 15 amp receptacles on a 20 amp circuit, provided that there is more than one receptacle on the circuit. A duplex receptacle counts as more than one receptacle. There are very few 120 volt devices that truly require a 20 amp circuit, and if they do (such as with an air conditioner or microwave), they usually require a dedicated circuit anyway.
The section is 210.52.
(B) Small Appliances
(1) Receptacle outlets served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20A small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Exception 2 allows a seperate, dedicated circuit for the fridge independent of the small-appliace circuits.
Basically, you must have 2 or more 20A circuits for small appliances that serve the above listed locations. If you only have 2 small appliance circuits, then they must also serve the dining areas. The dining areas can be served by a third (or fourth) 20A small-appliance circuit in addition to the two in the kitchen if you choose to have more than 2 small appliance circuits.
> You're saying that the dining room receptacles MUST be on the kitchen small appliance
> (countertop circuits)
No.
They can counted as such and, if so, may not serve loads or rooms that are not such.
If you pull a separate 20A circuit for your dining receptacles, I believe that you are fine.
It doesn't also have to be used in the kitchen.
It just can't serve the living room or bedroom etc.
You can also use more 15 or 20A general use circuits provided that a receptacle from a 20A small appliance circuit is available in the room too.
> Can you point me to a section of the NEC that states these requirements?
210.52.
No.
210.52.
Thanks guys. That was my plan; two 20A circuits dedicated to the kitchen couter tops. One 20A circuit covering the refrigerator (which would be ok under the section of the NEC you provided) and the dining room receptacles.
Sound ok?
Sound ok?
I use 15A (12/2 cable) for the fridge and avoid the GFCI.
This way, if you blow the breaker with some other appliances (toaster oven, George Foreman griddle, crockpots), the fridge is still running.
And you don't GFCI protect the fridge.
Why not pull another 20A circuit for the dining room?
You could put some kitchen receptacles on it too to bring more power to the kitchen.
This is at a minimum. Of course, pulling a new circuit for the dining room/other kitchen appliances and dedicating the refrigerator circuit is also an option (probably the one I will go with)
Originally Posted by fuente
What I was planning at a minimum was two gfi protected circuits for the coutertops.
One 20A non-gfi protected circuit for the fridge and the dining room circuits.
You are required to have lights also.
> I am not sure why I would go with 15A for the refrigerator/dining room circuit.
I wouldn't. 15A is if it is dedicated with a simplex receptacle.
Bedrooms require AFCI protection. Do you really want your living room and dining room to be AFCI protected as well?
210-12. Arc-Fault Circuit-Interrupter Protection
(a) Definition. An arc-fault circuit interrupter is a device intended to provide protection from the effects of arc faults by recognizing characteristics unique to arcing and by functioning to de-energize the circuit when an arc fault is detected.
(b) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere receptacle outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter(s). This requirement shall become effective January 1, 2002. (Graphic)
The 2005 NEC puts the requirement for AFCI protection on ALL outlets in a bedroom, which means lights, receptacles, and even smoke alarms. Local amendments may apply, so check them out.
#22
The 2005 code uses the term outlet. it does not include the term receptacle.
The term outlet (by itself) means receptacle, light, smoke detector, anything.
I am not going to type the code.
I do not know what the 2002 code says.
#23
ok thanks. so I guess that since I will be combining the lighting circuits for the dining, family and bedroom, it will need to be AFCI protected. No big deal. Thanks.
The other lighting circuit will serve the kitchen, family room and guest bath. AFCI protected?
The third will serve the other two bedrooms, master bath. Again, AFCI protected.
#24
For the 2005 NEC, anything electrical serving bedrooms needs to be AFCI protected.
Check if the 2005 code applies for your area, or if there are local ammendments that might apply.
Don't forget that you need interconnected smoke detectors for the house.