Wire size for 50 amp?
Old 03-19-06, 08:50 PM
Pendragon's Avatar
Received 2 Votes on 2 Posts
Just looking for wire size for a 50 amp connection.
Run is less than 4', 240v, (3+ground).
I'm thinking 6ga stranded or 8ga solid?
Old 03-19-06, 08:56 PM
just a quick question here,,
what you are planning to run with this much load on it ??
techally wise most 50 A load genrally use #6 wires BUT before i can get into more futher details please let us know what you will be running with it.
Merci, Marc
Old 03-19-06, 08:58 PM
Speedy Petey's Avatar
First off, for 240v you do NOT need 3 wires plus ground. NO neutral is required for straight 240v. Only two plus ground is required. If you did run 3 you would have no place to connect the neutral wire anyway.
Very basically, for a 50A circuit using NM cable you would need #6.
For THHN conductors in conduit you can go with #8cu.
Old 03-19-06, 09:37 PM
Is this a cooking appliance, a spa, a welder, or a subpanel feeder?
Old 03-20-06, 09:29 AM
Pendragon's Avatar
Interface conduction between generator connection and panel. (not mine).
I was looking at an appliance whip, since it's 6', already in conduit with fittings, it's 8ga THHN wire, and only $14 to boot. Would just need to feed a neutral wire through it.
"50 amp, 277 Volt Liquid-tight non-metallic 3/4" conduit. Pre-wired with 3 color coded 8 gauge THHN wires. One straight and one 90 deg. connector with reducing washers"
Old 03-20-06, 02:49 PM
So you DO have a 120/240v run, not simply a 240v run.
Do you have a transfer switch you are using?
Old 03-21-06, 07:38 PM
Pendragon's Avatar
I got a little more info.
This is basically about a 1.5' run between the generator plug and the transfer panel. He's going to need another cord to get from the generator to the plug.
I've got a length of UF-B, 8ga with 10ga ground. This is thick stranded wire, wrapped in a buriable sheathing. Would this work?
Old 03-22-06, 04:32 AM
No. UF is NM cable and #6 must be used.
Old 03-22-06, 09:37 AM
Pendragon's Avatar
Thanks.. I'll let him know he's just going to have to buy the wires individually.