Wire type for a 40A oven

Reply

  #1  
Old 03-23-06, 10:02 PM
Hooter's Avatar
Member
Thread Starter
Join Date: May 2005
Location: Phoenix "Its a dry heat" Arizona
Posts: 128
Wire type for a 40A oven

The new wiring for my oven needs to be #8 (40A) 4 wire. Can I use the wire that is like romax (NM) or do I need to use a conduit and use THHN?? I have up size most of my wire in this project and will likely use #6. If I use conduit, will the grey PVC meet code??
 
Sponsored Links
  #2  
Old 03-23-06, 11:34 PM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
> May I use the wire that is like romex (NM)?

Depends on local code.


> I have upsized most of my wire in this project and will likely use #6.

Great!


> If I use conduit, does grey PVC (RNC) meet code??

National Electric Code, yes.

Your local code, ???
 

Last edited by bolide; 03-24-06 at 01:45 PM.
  #3  
Old 03-24-06, 01:08 AM
Member
Join Date: Oct 2004
Location: USA
Posts: 719
Another words, every City makes changes to what they think is best, in this case you should ask your city's electrical inspector.
 
  #4  
Old 03-24-06, 03:11 AM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Originally Posted by bolide
> If I use conduit, does grey PVC (ENT) meet code??

National Electric Code, yes.

Your local code, ???
I see something that has confused me for about two months now. I saw ENT suggested to be used in a certain application and thought it was strange that it was suggested.

Bolide, ENT is not the grey pvc rigid conduit. Grey pvc is conduit, not tubing and is referred to as RNC, rigid non-metallic conduit.
ENT is electrical non-metallic tubing. That is the blue corrugated flexible tubing often referred to as "smurf" or "smurf tubing".
If you have a 2005 handbook you will see what I mean on pages 396 & 399.
 
  #5  
Old 03-24-06, 07:54 AM
Hooter's Avatar
Member
Thread Starter
Join Date: May 2005
Location: Phoenix "Its a dry heat" Arizona
Posts: 128
bolide......... My reference to code is the NEC... Phoenix uses the NEC as their code......With that said, will the NM meet code??
 
  #6  
Old 03-24-06, 09:58 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,337
Yes, the NEC allows a freestanding electric range circuit to be wired with 8/3g NM-B (Romex) cable and a 40A DP breaker for ranges 12kW or less; OR 6/3g NM-B (Romex) cable and a 50A DP breaker for larger ranges. Almost all ranges are less than 12kW, but feel free to use #6 if you want.
 